TDMM V13 page 3-6 (279) states that "Multiple telecommunications spaces on the same floor shall be interconnected with a minimum of one 78 mm (3 trade size) conduit or a pathway that provides equivalent capacity."
Multiple telecommunications spaces on the same floor shall be interconnected with a
minimum of two ≈103 mm (4 trade size) conduits or a pathway that provides equivalent
capacity.
Multiple telecommunications spaces on the same floor shall be interconnected with a
minimum of two ≈103 mm (4 trade size) conduits or a pathway that provides equivalent
capacity. Waldo mentioned the page.
Answer should be D: 2 x103mm (4 trade size) Chapter 3: page 3-4 Conduits, Trays, Slots, Sleeves, and Ducts
upvoted 4 times
...