TDMM 14 pg 3-4
"Multiple telecommunications spaces on the same floor shall be interconnected with a
minimum of two ~103 mm (4 trade size) conduits, or a pathway that provides equivalent
capacity."
TDMM V13 page 3-6 (279) states that "Multiple telecommunications spaces on the same floor shall be interconnected with a minimum of one 78 mm (3 trade size) conduit or a pathway that provides equivalent capacity."
Multiple telecommunications spaces on the same floor shall be interconnected with a
minimum of two ≈103 mm (4 trade size) conduits or a pathway that provides equivalent
capacity.
Multiple telecommunications spaces on the same floor shall be interconnected with a
minimum of two ≈103 mm (4 trade size) conduits or a pathway that provides equivalent
capacity. Waldo mentioned the page.
Answer should be D: 2 x103mm (4 trade size) Chapter 3: page 3-4 Conduits, Trays, Slots, Sleeves, and Ducts
upvoted 4 times
...
Log in to ExamTopics
Sign in:
Community vote distribution
A (35%)
C (25%)
B (20%)
Other
Most Voted
A voting comment increases the vote count for the chosen answer by one.
Upvoting a comment with a selected answer will also increase the vote count towards that answer by one.
So if you see a comment that you already agree with, you can upvote it instead of posting a new comment.
8e5c2e4
1 week agoJWL01
5 months, 3 weeks agoCUB90
1 year, 1 month agoRonLP
1 year, 8 months agoRonLP
1 year, 8 months agoLiONz5
2 years, 1 month agowaldo31
2 years, 2 months ago