You are designing a horizontal distribution system that will have a zone box located 71.6 m (235 ft) away from the telecommunications room (TR). A 50 mm (2 in) conduit is designed from the TR to a pull box located 36.6 m (120 ft) away from the TR. A 1 1/2 inch conduit is designed from the pull box to the zone box located
35.1 m (115 ft) beyond the pull box. Assuming no conduit bends, and excluding the TR and zone box, what is the total number of pull boxes/pull points required in this horizontal conduit system between the telecommunications room (TR) and zone box?